Autor Thema: Missing number in s-88 line.  (Gelesen 3107 mal)

Offline Nils Gullhav

  • Senior-Mitglied
  • Beiträge: 54
  • Ort: Norway Ort bei GoogleMaps suchen
Missing number in s-88 line.
« am: 03. Januar 2022, 10:38:47 »
Hei

We have a odd issue.
Litfinski usb interface line 1.  RM 1-240       (Ecos2 no s-88 in youse. WD 2021/2019)

It is in a big trainlift for 80 train.
Up to modul 14 ok.
Modul 15 dropping number 1. Count 2 as 1!!
That make a lot of trouble for the rest of modules in the line.

Will be happy for a solution to fix it :-)



Offline Stefan Lersch

  • Moderator
  • Senior-Mitglied
  • *
  • Beiträge: 6432
  • Ort: Brühl (bei Köln) Ort bei GoogleMaps suchen de
    • Infos zum Down-Syndrom alias Trisomie 21
Re: Missing number in s-88 line.
« Antwort #1 am: 03. Januar 2022, 13:14:48 »
Hello Nils,

please check in the system settings of WDP if all feedback contacts are entered correctly. I guess that there is a mistake in module 15. Do you already use WDP 2021? There, in the graphical display, you can see directly which feedback port corresponds to which feedback number. Maybe they are shifted 1 to the right.
Viele Grüße,
Stefan
  • Win-Digipet-Version:
    WDP 2021.x Beta
  • Anlagenkonfiguration:
    N-Anlage im Bau, Minitrix &amp Co., Tams MC 2.2.3, DCC
  • Rechnerkonfiguration:
    Quad Core 8 GB mit Win 10, 32"quot Bildschirm

Offline Nils Gullhav

  • Senior-Mitglied
  • Beiträge: 54
  • Ort: Norway Ort bei GoogleMaps suchen
Re: Missing number in s-88 line.
« Antwort #2 am: 03. Januar 2022, 14:54:57 »
Hei
Yes we youse 2021 :-)
Fast delivering I Norway  ;)
I did update as at try to fix.

The trouble started with 2018.
But my friend has put on 80 train in the lift. And then he start to program fb in the layout.
Did the trouble start. We all now it is not easy to se fb when all is occupied

The setup for s-88 looks correct.
And it is not many wrong setting you can sett on the line of the Litfinski usb.
The line start with fb1 modul 1. And last number entering by it self.
And it is correct numbers in the line.

We have tested with a new S-88 in front of the number as missing.
And insted the box so missing 1.fb and 2.input registrer as 1fb in
And that don't help.

Offline Nils Gullhav

  • Senior-Mitglied
  • Beiträge: 54
  • Ort: Norway Ort bei GoogleMaps suchen
Re: Missing number in s-88 line.
« Antwort #3 am: 03. Januar 2022, 21:01:51 »
We did find the reason.

Interfirens from trafo in 2pc off CAT cable.

One between box 4-5
And to the last box.

Nils :-)